This is in reference to a piece of equipment with an integral control panel incorporating a thru-door main disconnect with the main load being a motor. I have been noticing lately manufacturers of packaged equipment utilizing a motor circuit protector type circuit breaker as opposed to a traditional thermal magnetic circuit breaker. Traditionally, with a thermal mag main disconnect, we design the upstream feeder breaker to match the control panel's main breaker with a full size feeder. Or sometimes we go a little heavy; say the panel disconnect is a 175A breaker, we may size a 200A feeder.
However, with the motor circuit protector breakers, you can't simply match the breaker amperage with the upstream feeder. This is because the feeder breaker would be a thermal magnetic and the motor circuit protector breaker will handle the motor inrush and push this to the feeder thermal mag which may trip. So the question is, have anybody else been seeing this and how do you size the feeder and upstream CB if the control panel main disconnect is a motor circuit protector? Lately we have just been specifying the control panel main needs to be a thermal mag, but sometimes we run into pre-purchased equipment.
However, with the motor circuit protector breakers, you can't simply match the breaker amperage with the upstream feeder. This is because the feeder breaker would be a thermal magnetic and the motor circuit protector breaker will handle the motor inrush and push this to the feeder thermal mag which may trip. So the question is, have anybody else been seeing this and how do you size the feeder and upstream CB if the control panel main disconnect is a motor circuit protector? Lately we have just been specifying the control panel main needs to be a thermal mag, but sometimes we run into pre-purchased equipment.