timosborne
Member
As part of an energy savings initiative, we recently installed VFD's on multiple air-handling units in our facility. The previous motor circuit for each unit consisted of a Square D Mag-Gard motor circuit protector and starter w/ overloads in MCC bucket feeding the respective unit. We removed starter in bucket circuit and wired directly tp MCP. The VFD was installed at the unit. We were told we violated code section 240.4 that states that all current carrying conductors shall be protected against overcurrent in accordance with their ampacities specified in 310.15. The reviewer stated that MCP's do not provide overcurrent protection and we need to replace the MCP with a thermal magnetic breaker.
The way I understand it is that the MCP provides instantaneous-trip magnetic-only and when installed as part of a UL Listed combination controller having motor overload protection it is code compliant. The VFD we installed does have thermal protection capability. From what I've understood, the thermal overload protection can be anywhere in the circuit between the motor & the overcurrent protection device at the source correct - not always at the start of the circuit/source? I believe we have that with the VFD's ability to provide thermal overload protection or do we have a code issue? VFD does not have bypass.
Do we need to replace all MCP's with thermal-mags as stated by the reviewer?
Thanks,
The way I understand it is that the MCP provides instantaneous-trip magnetic-only and when installed as part of a UL Listed combination controller having motor overload protection it is code compliant. The VFD we installed does have thermal protection capability. From what I've understood, the thermal overload protection can be anywhere in the circuit between the motor & the overcurrent protection device at the source correct - not always at the start of the circuit/source? I believe we have that with the VFD's ability to provide thermal overload protection or do we have a code issue? VFD does not have bypass.
Do we need to replace all MCP's with thermal-mags as stated by the reviewer?
Thanks,