All check my calculations. 30HP motor 480V design A. From 430.250 40amps. 40amps X 125%= 50amps. 110.14(c)(1) unless marked for 75 use 60 column in 310.15. Only other exception that I saw that would apply is the design which is not B, C or D. I sized the wire at 6AWG. My next question is the disconnect. The current disconnect is a 20HP but is rated for 60amps. 430.110 115% X 40amps = 46amps. I believe the disconnect is ok. I always sized my disconnects to the HP of the motor but the 115% in this case is ok compared to the disconnect amperage rating.
Manufacturer ran 10awg from the controller (which is sized at 30HP) to the disconnect and motor. I say big problem here. My only area of concern is that there is a soft start after the contactor. Does the soft start allow for reduced wire size? I don't think so but any info would be helpful. Thanks!