paac
- Lapeer, MI
I have a study question regarding a motor circuit that I need some clarification on. Just trying to see if I'm figuring this out correctly. I apologize in advance for the length of this. Hopefully it is readable.
I'm in Michigan, so this will be based on 2005 code.
Motor is 20HP, 230V, 3 phase, 48A FLC (nameplate), 1.0 SF, Design B. Will be using time delay, dual element fuses for overcurrent protection.
Disconnect:
Per 430.109 and .110, I need a disconnect rated not less than 115% of FLC. FLC according to Table 430.250 is 54A. 54 x 1.15 = 62.1A. So I need a disc rated not less than 70A, correct?
Branch Circuit SC and GF protection:
Table 430.52 Design B gives multiplier as 175% of FLC. 1.75 x 54 = 94.5.
430.52(C)(1) requires protective device NOT EXCEEDING values in table, but then states in ex #1 that you can use the next higher size if it doesn't correspond to standard sizes or ratings of fuses, etc.
240.6 gives 90 and 100 as standard sizes. I am assuming my answer would be 90, but could I use 100? Is this where hard start and easy start comes into play?
Motor Circuit Conductors:
430.22(A) requires 125% FLC. 1.25 x 54 = 67.5.
Per T310.16, I get #4 copper.
Overloads:
Motor has SF of 1.0 and gives no temp rise, so per 430.32(A)(1) I will use 115% of nameplate FLC for my overloads. 1.15 x 48 = 55.2.
Equipment Grounding Conductor:
In sizing the egc, 430.245 refers to part VI of art. 250. Using Table 250.122 and a fuse size of 90A, I come up with #8 copper.
Am I using the correct overcurrent device in my calculations (assuming 90A is the correct size)?
Thanks in advance for any input.
Disconnect:
Overloads: