I have a study question regarding a motor circuit that I need some clarification on. Just trying to see if I'm figuring this out correctly. I apologize in advance for the length of this. Hopefully it is readable.
I'm in Michigan, so this will be based on 2005 code.
Motor is 20HP, 230V, 3 phase, 48A FLC (nameplate), 1.0 SF, Design B. Will be using time delay, dual element fuses for overcurrent protection.
Disconnect:
Per 430.109 and .110, I need a disconnect rated not less than 115% of FLC. FLC according to Table 430.250 is 54A. 54 x 1.15 = 62.1A. So I need a disc rated not less than 70A, correct?
Branch Circuit SC and GF protection:
Table 430.52 Design B gives multiplier as 175% of FLC. 1.75 x 54 = 94.5.
430.52(C)(1) requires protective device NOT EXCEEDING values in table, but then states in ex #1 that you can use the next higher size if it doesn't correspond to standard sizes or ratings of fuses, etc.
240.6 gives 90 and 100 as standard sizes. I am assuming my answer would be 90, but could I use 100? Is this where hard start and easy start comes into play?
Motor Circuit Conductors:
430.22(A) requires 125% FLC. 1.25 x 54 = 67.5.
Per T310.16, I get #4 copper.
Overloads:
Motor has SF of 1.0 and gives no temp rise, so per 430.32(A)(1) I will use 115% of nameplate FLC for my overloads. 1.15 x 48 = 55.2.
Equipment Grounding Conductor:
In sizing the egc, 430.245 refers to part VI of art. 250. Using Table 250.122 and a fuse size of 90A, I come up with #8 copper.
Am I using the correct overcurrent device in my calculations (assuming 90A is the correct size)?
Thanks in advance for any input.
I'm in Michigan, so this will be based on 2005 code.
Motor is 20HP, 230V, 3 phase, 48A FLC (nameplate), 1.0 SF, Design B. Will be using time delay, dual element fuses for overcurrent protection.
Disconnect:
Per 430.109 and .110, I need a disconnect rated not less than 115% of FLC. FLC according to Table 430.250 is 54A. 54 x 1.15 = 62.1A. So I need a disc rated not less than 70A, correct?
Branch Circuit SC and GF protection:
Table 430.52 Design B gives multiplier as 175% of FLC. 1.75 x 54 = 94.5.
430.52(C)(1) requires protective device NOT EXCEEDING values in table, but then states in ex #1 that you can use the next higher size if it doesn't correspond to standard sizes or ratings of fuses, etc.
240.6 gives 90 and 100 as standard sizes. I am assuming my answer would be 90, but could I use 100? Is this where hard start and easy start comes into play?
Motor Circuit Conductors:
430.22(A) requires 125% FLC. 1.25 x 54 = 67.5.
Per T310.16, I get #4 copper.
Overloads:
Motor has SF of 1.0 and gives no temp rise, so per 430.32(A)(1) I will use 115% of nameplate FLC for my overloads. 1.15 x 48 = 55.2.
Equipment Grounding Conductor:
In sizing the egc, 430.245 refers to part VI of art. 250. Using Table 250.122 and a fuse size of 90A, I come up with #8 copper.
Am I using the correct overcurrent device in my calculations (assuming 90A is the correct size)?
Thanks in advance for any input.