I have a question on tapping from a busbar to a single motor that
hopefully you can shed some light on.
I have a 32hp, 460v, 3ph motor (lathe) which has an internal overload
~40amp fuse and 75amp CB in its control panel and I was going to feed
this with a 100amp plug-in circuit breaker (mounted 30feet away) with
#8 AWG THHN. My concern is the wire size - I originally thought #8 is
adequate with 40A FLC x 1.25 = 50 since this is for a motor.
However, now considering the tap rule and that the machine is located
more than (10 or the 25feet away) - Does this change my conductor and
plug-in CB? How do you size for this?
Thanks in advance for your help!