I'm tring to wire a motor for a spa blower for a Hotel.
It's rated at 110/230V 17.8/8.9A 2HP
I wired it for 230V, but I got 208V 1PH from a 3PH panel. It's about 20' from the panel to the timeclock and then about 150' to the motor (via a 2pole toggle switch for disconnect)
Now check at the disconnect, which is 5' from the motor I check voltage. Without the motor running I have 208V, I turn on the disconnect, and as the motor is starting up, the voltage goes to 190V and when the motor is running it's at 200V.
The motor runs for about 5 to 10 minutes then the thermal protection in the motor shuts off, until the motor cools down.
I ran the ckt in #12 wire. mc for about 100 feet then goes in jbox and switches over to PVC and THHN.
Now I was gonna change the wire to #10 for voltage drop.
But my Question is should I also wire it for 110V since I have 120V or should a motor rated at 230V work fine with 208V??????????
It's rated at 110/230V 17.8/8.9A 2HP
I wired it for 230V, but I got 208V 1PH from a 3PH panel. It's about 20' from the panel to the timeclock and then about 150' to the motor (via a 2pole toggle switch for disconnect)
Now check at the disconnect, which is 5' from the motor I check voltage. Without the motor running I have 208V, I turn on the disconnect, and as the motor is starting up, the voltage goes to 190V and when the motor is running it's at 200V.
The motor runs for about 5 to 10 minutes then the thermal protection in the motor shuts off, until the motor cools down.
I ran the ckt in #12 wire. mc for about 100 feet then goes in jbox and switches over to PVC and THHN.
Now I was gonna change the wire to #10 for voltage drop.
But my Question is should I also wire it for 110V since I have 120V or should a motor rated at 230V work fine with 208V??????????