motor/conductor feeder and branch circuit scgf protection
mistake.
Thanks for helping me clear this up. i would appreciate a little more info if you don't mind. I have seen a lot of fused disconnects providing scgf protection and in some cases none or i assumed none. Can you tell me how you determined a 70 amp breaker would be sufficient and do you know if a 60 amp would be ok? I'm feeding two 20hp motors, 3phase,480v with separate circuits in a single conduit for around 150'. These motors are being provided by a company for air blowers and they specified 60amp breakers and they provided the motor controllers with overload protection for each motor. The motors will be approximately the full 150' away from the controllers and the controllers will be right next to the load center (breaker).
Thanks again :thumbsup: