I have a single 150HP VFD driving two 75hp motors. I have individual thermal overloads for each motor. The motor leads from the OL's to each motor are what I'm questioning.
According to 430.22 I need to size the conductors for 125% of 96 amps (From table 430.250) or 120 Amps. Which would indicate I need an 1 AWG motor conductor, correct ?
The motor itself has size 4 AWG leads coming out of the motor. Is this normal to see this large difference in conductor sizes ?
BTW the name tag FLA is 88.5A
Thanks for any input..
According to 430.22 I need to size the conductors for 125% of 96 amps (From table 430.250) or 120 Amps. Which would indicate I need an 1 AWG motor conductor, correct ?
The motor itself has size 4 AWG leads coming out of the motor. Is this normal to see this large difference in conductor sizes ?
BTW the name tag FLA is 88.5A
Thanks for any input..