Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
Reading and article and it stated this ….
For motors marked with design letters B, C, or D, you can use conductors having an insulation rating of 75°C or higher if the ampacity of such conductors doesn’t exceed the 75°C ampacity listed in Table 310.15(B)(16) [110.14(C)(1)(a)(4)].
..does this mean that no matter what , if terminals are 90 degree or if using correction factors etc., basically anything that would allow you to use the 90 degree column you CAN’T?
Also, it stated this…
For equipment rated 100A or less, you must size the conductors using the 60°C temperature column of Table 310.15(B)(16) [110.14(C)(1)(a)(2)].
…are there exceptions to this where you can use the 75 or 90 degree column? Id have to imagine so as a lot of the loads we use when sizing are under 100a and we rarely use the 60 degree column .