We have a differences of opinions in our office. Your advice will be welcome.
When sizing a single motor circuit. Can the conductors from a distribution panelboard to a combination motor starter be sized at 125% of the Full load current of the motor or must it be sized to the circuit breaker in the distribution panelboard. That circuit breaker can be sized up to 250% of the motor full load current. I didn't think that the conductors on the line side of the combination motor starter had to exceed the 125% of the motor load...
When sizing a single motor circuit. Can the conductors from a distribution panelboard to a combination motor starter be sized at 125% of the Full load current of the motor or must it be sized to the circuit breaker in the distribution panelboard. That circuit breaker can be sized up to 250% of the motor full load current. I didn't think that the conductors on the line side of the combination motor starter had to exceed the 125% of the motor load...