Steve McKinney
Member
Having a dilema fellas. Last night in class we were going over motor branch circuits. I was telling the class that the 240.4 (D) did not apply to motor circuits. As you know, if you look at T310.16, the asterik will tell you to go to 240.4D. This is the #10 on 30 amp, # 12 on a 20 amp ocp and #14 on a 15 amp ocp. It also tells you to look at 240.4 (E) and 240.4 (G), which is the table for "Specific Conductor Applications".
My dilema is that Motor and motor-control circuit conductors is listed with "430, Parts III, IV, V, VI, VII"
Motor circuit conductors is Part II!
How do I read this? MY problem is that I am looking to justify the branch circuit conductor to be utilized at their rated values per T 310.16 and not being obligated to tie a #10 to a maximum 30 amp breaker.
How can I best explain this Gentlemen?
Thnx in advance,
Steve McKinney
My dilema is that Motor and motor-control circuit conductors is listed with "430, Parts III, IV, V, VI, VII"
Motor circuit conductors is Part II!
How do I read this? MY problem is that I am looking to justify the branch circuit conductor to be utilized at their rated values per T 310.16 and not being obligated to tie a #10 to a maximum 30 amp breaker.
How can I best explain this Gentlemen?
Thnx in advance,
Steve McKinney