I recently had a discussion with an engineer, about motors that are frequently failing on one of our lines. Some background on the motors;
Bodine Motor; Volts 208-240/360-415AC, Amps 1.3-1.6/0.7-0.9, Rev/Min 1700, KW .210, 50 cycle. Rated for continuous duty. Motors are used on conveyor system carrying minimal load. Feed to motors are 480 volt Ungrounded Delta.
Motors are continually failing, but no one can come up with the reason why. The bearings on the motor seem to be failing due to excessive heat. There is much speculation on why, but no one can come up with the answer.
The engineer said that the problem may be with the service. He said that the (main service) if connected Delt and not Y connection may have an effect on these motors. Did anyone run into a problem like this before????? Also, voltage drop for a motor 5% or 10%????
Other lines using the same motors are not having a problem.