Can someone describe the differences between these two for me please? The lighting contactor seems to be a lot more expensive than the motor contactor.
In that case, if they're to all be switched together (and presuming they lights have their own panel), you might want a single large contactor to switch the entire panel.
A NEMA Size 1 motor starter is continuous rated 27A for motor starting and only 15A for "tungsten lamp loads" (fluorescent lamp loads are treated like motor loads).
When you say fluorescent lamps loads are treated like motor loads are you referring to the fact that they strive to produce a constant power output.
I was looking at a particular 100W light recently and noticed that it had a multi-tapped ballast and that with lower voltage the light drew more current. I would think that a light would act more or less as a resistive element, and therefore a reduced voltage input would create a reduced current draw. Is there something in the ballast that causes the light to produce constant power and thus exhibit this relationship?
I was strictly addressing the construction on the contacts of the controller. In this regard, the power factor and inrush magnitude and duration of a fluorescent ballast are similar to those of induction motors.When you say fluorescent lamps loads are treated like motor loads are you referring to the fact that they strive to produce a constant power output.
Yes. In a magnetic ballast, that would be the multiple taps on the primary winding, like a multi-voltage control transformer in an HVAC unit. In an electronic ballast, the circuitry uses whatever current is necessary to maintain the required power level, at the voltage supplied to it.I was looking at a particular 100W light recently and noticed that it had a multi-tapped ballast and that with lower voltage the light drew more current. I would think that a light would act more or less as a resistive element, and therefore a reduced voltage input would create a reduced current draw. Is there something in the ballast that causes the light to produce constant power and thus exhibit this relationship?
Added: There's a profound difference between applying different voltages to a given impedance, and applying different voltages to equipment designed for those differences. The multi-tap ballast is basically the same as having ballasts with different voltage ratings.