I have a question concerning the motor disconnect means, whether or not this is required by codes and standards to be interlocked with the motor controller circuit, when the second disconnect (the motor disconnecting means) is required to meet the 50 foot ruler. The Controller disconnecting means is not lockable, out of sight, and more than fifty feet away. Also, if an aux contact in the motor disconnect is required to be interlocked with the motor controller circuit to prevent possible unexpected start up when the motor disconnect is closed, would lockout tag out procedure permit this interlock (providing it is required) to be omitted? Or would the motor disconnecting means be required to disconnect the control power in its entirety to the motor control circuit via an additional contactor at the controllers control power transformer or by two aux contacts within the motor disconnecting means.
I have heard of situations of motor disconnects being closed and motors inadvertently starting because someone initiated the start command (pressing the start button and walking away), Later when maintenance is complete the motor disconnect is closed and the motor immediately starts.
What are your thoughts?
Motor in Question:
10 Hp, 3-Ph, 460 V
Part of a multi-motor process
Industrial environment
Multiple stop start locations.
Thanks for your time,
Frank Brux
Edited to remove your e-mail address and phone number. Please use the PM (private messaging) system and trade e-mail address and/or phone numbers there.
Thanks,
Charlie
[ November 29, 2004, 12:54 PM: Message edited by: charlie ]
I have a question concerning the motor disconnect means, whether or not this is required by codes and standards to be interlocked with the motor controller circuit, when the second disconnect (the motor disconnecting means) is required to meet the 50 foot ruler. The Controller disconnecting means is not lockable, out of sight, and more than fifty feet away. Also, if an aux contact in the motor disconnect is required to be interlocked with the motor controller circuit to prevent possible unexpected start up when the motor disconnect is closed, would lockout tag out procedure permit this interlock (providing it is required) to be omitted? Or would the motor disconnecting means be required to disconnect the control power in its entirety to the motor control circuit via an additional contactor at the controllers control power transformer or by two aux contacts within the motor disconnecting means.
I have heard of situations of motor disconnects being closed and motors inadvertently starting because someone initiated the start command (pressing the start button and walking away), Later when maintenance is complete the motor disconnect is closed and the motor immediately starts.
What are your thoughts?
Motor in Question:
10 Hp, 3-Ph, 460 V
Part of a multi-motor process
Industrial environment
Multiple stop start locations.
Thanks for your time,
Frank Brux
Edited to remove your e-mail address and phone number. Please use the PM (private messaging) system and trade e-mail address and/or phone numbers there.
Thanks,
Charlie
[ November 29, 2004, 12:54 PM: Message edited by: charlie ]