I am about to install a feeder circuit for a new motor control box, which controls three(3) single-phase 15 HP motors. The nameplate rating on each motor is 48.4 Amps. These are for a community water pumping station, and at least one of these motors will be operating on a continuous basis. While it is possible that all 3 can operate simultaneously, it is highly unlikely, or would be considered a rare circumstance.
According to table 430-248, a 10 HP single phase motor operating at 230 Volts draws 50 Amps. So, either these are super-efficient motors, or the owner was mis-informed as to the actual HP rating of them.
Table 430-248 does not show anything above 10 HP, so does this mean there is no such thing as a 15 HP single phase motor, or ...?
In trying to calculate the proper feeder size for this scenerio, I come up with the following:
3x48.4 Amps = 145.2 Amps
25% of largest motor = 12.1 Amps
Total calculated required circuit capacity = 157.3 Amps
With this result, I figure we would need to install a 2/0 THHN feeder, protected by an inverse-time circuit breaker whose rating could be up to 400 Amps. (I plan to use a 200 Amp breaker at the onset).
Is there anything I'm missing on this?
Edit to add:
The building is existing, and has a 400 Amp single phase service there.
3 phase service is not available in that area.
These pumps will replace an existing array currently fed with a 125 Amp rated feeder.
According to table 430-248, a 10 HP single phase motor operating at 230 Volts draws 50 Amps. So, either these are super-efficient motors, or the owner was mis-informed as to the actual HP rating of them.
Table 430-248 does not show anything above 10 HP, so does this mean there is no such thing as a 15 HP single phase motor, or ...?
In trying to calculate the proper feeder size for this scenerio, I come up with the following:
3x48.4 Amps = 145.2 Amps
25% of largest motor = 12.1 Amps
Total calculated required circuit capacity = 157.3 Amps
With this result, I figure we would need to install a 2/0 THHN feeder, protected by an inverse-time circuit breaker whose rating could be up to 400 Amps. (I plan to use a 200 Amp breaker at the onset).
Is there anything I'm missing on this?
Edit to add:
The building is existing, and has a 400 Amp single phase service there.
3 phase service is not available in that area.
These pumps will replace an existing array currently fed with a 125 Amp rated feeder.