Hello,
I have a combination starter with a 480-120V, 500VA control transformer tapped from the load side of the branch circuit protective device. Within the 120V control circuit is a remote sensor that requires a factory assembled cordset.
Based on the transformer specifications, I believe this would be classified as a Class 1 remote-control and signaling circuit. If the circuit is classified in this way, the factory assembled corset would not meet the requirements of 725, as it is rated 250V, 4A.
However, I believe a solution would be to find a cable specified as ITC (Instrumentation Tray Cable). This would fall under the provisions of article 727 and article 725 would not apply.
Am I applying this correctly?
Thanks.
I have a combination starter with a 480-120V, 500VA control transformer tapped from the load side of the branch circuit protective device. Within the 120V control circuit is a remote sensor that requires a factory assembled cordset.
Based on the transformer specifications, I believe this would be classified as a Class 1 remote-control and signaling circuit. If the circuit is classified in this way, the factory assembled corset would not meet the requirements of 725, as it is rated 250V, 4A.
However, I believe a solution would be to find a cable specified as ITC (Instrumentation Tray Cable). This would fall under the provisions of article 727 and article 725 would not apply.
Am I applying this correctly?