Need some guidance for a service feed for a motor control panel.
The 480 panel will feel 9, 3p, 18hp motors and 9, 3p, 5hp motors. Each motor will have 120v control circuit, and the 5hp motors will have a temperature controller.
The 15hp motors are used for pumping oil in/out, the 5hp motors are used to heat up the oil.
Here is the tricky part:
The motors cannot all run at the same time. Only one blender is able to pump at once, and all heat exchangers won't be used at once. What is the minimum service feed we can add for this panel? The contractor we first talked to wants to add a 200 amp service, which would align with the scenario of all motors running at once. That would require a 500' run from our main MCC. Another option is underrating the panel and feeding out of a subpanel, but this needs to be within code.
What is code for the minimum usage? We have existing panels with up to 20 motors on a 100 amp circuit.
The 480 panel will feel 9, 3p, 18hp motors and 9, 3p, 5hp motors. Each motor will have 120v control circuit, and the 5hp motors will have a temperature controller.
The 15hp motors are used for pumping oil in/out, the 5hp motors are used to heat up the oil.
Here is the tricky part:
The motors cannot all run at the same time. Only one blender is able to pump at once, and all heat exchangers won't be used at once. What is the minimum service feed we can add for this panel? The contractor we first talked to wants to add a 200 amp service, which would align with the scenario of all motors running at once. That would require a 500' run from our main MCC. Another option is underrating the panel and feeding out of a subpanel, but this needs to be within code.
What is code for the minimum usage? We have existing panels with up to 20 motors on a 100 amp circuit.