Re: MOTOR Control protection
The motor overload devices are often integrated into the motor starter. But, you can use a separate overload device such as a dual-element fuse (usually located near the motor starter, not the supply breaker). If you use fuses, you must provide one for each ungrounded conductor [430.36 and 430.55]. Thus, a three-phase motor requires three fuses. Keep in mind that these devices are at the load end of the branch circuit and they do not provide short-circuit and ground-fault protection.
Motors rated more than 1-hp (without integral thermal protection) and motors 1-hp or less (automatically started) [430.32(C)], must have an overload device sized per the motor nameplate current rating [430.6(A)]. You must size the overload devices no larger than the requirements of 430.32. Motors with a nameplate service factor (S.F.) rating of 1.15 or more must have the overload protection device sized no more than 125 percent of the motor nameplate current rating.