Motor control switch as feeder disconnect?

Status
Not open for further replies.

Soundside

New User
Location
Newport News
Occupation
Health Physics
Is it acceptable to use a motor control switch, such as Siemens HNF3060CJ as a safety disconnect, such as for a feeder to an out building?
 
Per your occupation, this could be a DIY post. Can you clarify what type outbuilding and why you want to use the contractor?
Click on my name to send msg
 
Is it acceptable to use a motor control switch, such as Siemens HNF3060CJ as a safety disconnect, such as for a feeder to an out building?
Although still pending your status, the answer to your question is NO. That type of switch is only listed to be used as the LAST switch in a motor Branch circuit. It is not listed to be used as a Feeder,
 