When using a manual motor controller for overload protection can the hp rating of the controller be less than the motor as long as it can be set for flc of motor.
example: 460v-15hp pump @ 3450rpm = 18.2fla
Which of the following controllers should be used?
1) rated 10hp@460 with setting range 16-20amps.
2) rated 15hp@460 with setting range 20-25amps.