I would say it's a violation of 404.8(A) unless the motors happened to be at that height as well.faresos said:I was inspectin an electric room and found two starters mounted on a top of panelboard at approx. 7'-6". Those staters have Auto/Manual/off selector. Is this installation a code violation since it's above 6'-7"? Thanks,
I have to disagree. OP states they have HOA control on them which in my opinion is a switch. 404.8(A) says All switches and circuit breakers used as switches shall be located so that they may be operated from a readily accessible place. They shall be installed such that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 6ft. 7in. above the floor or working platform.benaround said:Chevy,
404.8 A is more about switches and circuit breakers IMO, I don.t see a
problem with the starters above the panel. I'll look to see if I can get a code
reference to back it up.
Read post #2.SouthNJ said:What about Exception #2 in Art. 404.8? If the motors are nearby this should be ok and you have a ladder handy.