coulter said:Could one of you explain why the overloads did not shut down the soft start?
carl
Interesting. This has not been my experience. I've probably worked with six, ranging from 60hp to 350hp, over the last 20 years. Should be firing up a 600hp next year. All were AB SMC, so my experience is limited. All were programmable to trip before damage from overload. The one tech manual I have in front of me cautions one must not exceed the Soft Start Nameplate ratings when setting the motor FLA.Jraef said:..An OL relay will trip (assuming class 10) in 10 seconds at 600% current, but maybe 2-3 hours at only 118% current. It is meant to protect the motor, not the controller. At 118% current the soft starter would overheat and the SCRs short. the soft starter should have had a heat sink over-temp switch, but usually by the time that trips it's too late, kind of like an "idiot light".
Jraef said:Frenchelectrician,
I think you missed the fact that this was a soft starter, not a VFD.
An OL relay will trip (assuming class 10) in 10 seconds at 600% current, but maybe 2-3 hours at only 118% current. It is meant to protect the motor, not the controller. At 118% current the soft starter would overheat and the SCRs short. the soft starter should have had a heat sink over-temp switch, but usually by the time that trips it's too late, kind of like an "idiot light".