Not going to get into to too many details but here is what I have going on.
Recently a failed 200H.P. motor (460VAC, 1.15 SF, Design B, 400A MCP, size 5 starter, 350MCM feeder) was replaced with a manufactured 250H.P. motor (460VAC,SF 1.15, Design B).
The application is a PD boiler feed water pump. The replacement manufactured 250 H.P. motor has a name plate of 200H.P., per the vendor the motor “de-rated” from 250H.P. to 200H.P. Per the vendor I was assured that this is essentially a “200H.P.” motor.
What I’m having trouble grasping is:
Is the vendor correct on his statement of the de-rated motor?
Is the FLA/inrush of the "250H.P. manufactured" motor per a 250H.P. or 200H.P.?
Will the starter size still be 5? (cut off for 5 is 200H.P.)
Will calculations for feeder cable, MCP settings, and OL be calculated from a size of 200H.P. or 250H.P.?
Just having a little trouble getting my head around this.
Thanks a bunch
Recently a failed 200H.P. motor (460VAC, 1.15 SF, Design B, 400A MCP, size 5 starter, 350MCM feeder) was replaced with a manufactured 250H.P. motor (460VAC,SF 1.15, Design B).
The application is a PD boiler feed water pump. The replacement manufactured 250 H.P. motor has a name plate of 200H.P., per the vendor the motor “de-rated” from 250H.P. to 200H.P. Per the vendor I was assured that this is essentially a “200H.P.” motor.
What I’m having trouble grasping is:
Is the vendor correct on his statement of the de-rated motor?
Is the FLA/inrush of the "250H.P. manufactured" motor per a 250H.P. or 200H.P.?
Will the starter size still be 5? (cut off for 5 is 200H.P.)
Will calculations for feeder cable, MCP settings, and OL be calculated from a size of 200H.P. or 250H.P.?
Just having a little trouble getting my head around this.
Thanks a bunch