Motor disconnect question

Status
Not open for further replies.

guitarsarge

Member
Location
Texas
I'm confused with the answer to this one:

What size disconnecting means is required for a single 5 HP 115V motor on a separate branch circuit?

a. 30A
b. 60A
c. none of these
d. 100A

I came up with 64.4A, so I chose (c) thinking the next size up would be 70A.

Answer is 100A, but I don't understand why. Can someone shed some light for me?

Thanks
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I can only assume that since to many, especially us old timers, motor disconnect" means switch and the next size switch above a 60 is a 100.
The question was probably designed to see if you knew the 60 amp switch on a motor with a FLA of 56 was not sufficient.
 

guitarsarge

Member
Location
Texas
Lol, ok. I don't work with motors at all and I've never seen that in print. Where can I find a list of switches for motors and the standard Ampere ratings?
 

RonPecinaJr

Senior Member
Location
Rahway, NJ
Lol, ok. I don't work with motors at all and I've never seen that in print. Where can I find a list of switches for motors and the standard Ampere ratings?

Single phase and three phase motor ampere ratings -- tables 430.247-430.251

NEC 430.110

Disconnect ampere ratings requires the disconnect be rated 115% of the the full-load current rating of the motor.

56 amps x 1.15 = 64.4 amps

That's why you need to go with the 100 amp disconnect.
 

guitarsarge

Member
Location
Texas
Single phase and three phase motor ampere ratings -- tables 430.247-430.251

NEC 430.110

Disconnect ampere ratings requires the disconnect be rated 115% of the the full-load current rating of the motor.

56 amps x 1.15 = 64.4 amps

That's why you need to go with the 100 amp disconnect.

Thanks, I understand how to do the calculation though. I'm looking for the standard ampere ratings for motor switches. So far I know there is a 60 A and 100A. I'm looking for something similar to 240.6 standard ampere ratings, but for motor switches.
Any help appreciated.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Check any gear catalog (GE, SqD, Cutler-Hammer etc)
but basically 0,60,100,200,400,600,800,1200 amps
 