First off, thank you very much for the opportunity to join the forum. I realize the are some very talented people in these forums.
I recently purchased a new compressor and I am trying I to size a disconnect for the motor
Motor specs:
Baldor
5hp
Single phase
240v
23 amps (nameplate)
From table 430 in NEC the flc for a 5hp single phase motor is 28 amps. Taking 115% of the flc produces 32 amps. I am curious because there are a lot of disconnects are rated at 30 amps and 5hp @ 240v. How is this?
Also it appears that most of the disconnects are sized for #8-10 awg. I ran #6 awg for the feeder circuit (magnetic starter/overload protection is wired with #8 awg. I am having a hard time finding a disconnect that will work for this application. The disconnect needs to accommodate #6 and #8awg. Do you guys have any recommendations?
First off, thank you very much for the opportunity to join the forum. I realize the are some very talented people in these forums.
I recently purchased a new compressor and I am trying I to size a disconnect for the motor
Motor specs:
Baldor
5hp
Single phase
240v
23 amps (nameplate)
From table 430 in NEC the flc for a 5hp single phase motor is 28 amps. Taking 115% of the flc produces 32 amps. I am curious because there are a lot of disconnects are rated at 30 amps and 5hp @ 240v. How is this?
Also it appears that most of the disconnects are sized for #8-10 awg. I ran #6 awg for the feeder circuit (magnetic starter/overload protection is wired with #8 awg. I am having a hard time finding a disconnect that will work for this application. The disconnect needs to accommodate #6 and #8awg. Do you guys have any recommendations?