Davebones
Senior Member
- Location
- North Of Tampa Fl
Have a 150 hp 480V 3 Phase motor . I understand the the current draw is 180 amps . I figure at 115 % gives us 207 amps ( 430.110 ) for size of disconnect .Am I correct to understand I can't use a 200 amp fusible switch even if I mark it "do not disconnect under load " ??????