I always see these Eaton Heavy Duty Safety Switches that serve compressors or motors, but they only have the ampere rating and voltage (400A, 600V for example). I also always see the ampere rating on single line diagrams but they don't usually indicate the HP rating. Looking at 430.109(A)(1) it appears that the code requires the switch to be rated for the HP of the motor. But then I see 430.110(A) which only talks about Ampere Rating but doesn't really require the switch to be rated for the motor HP. Does the switch need to be rated in ampere and HP for a motor load?
Also, section 430.109(E) talks about an isolating switch for motors over 100HP, but what about motors below this but above 2HP? Also, 430.109(E) says that the switch should be marked "Do not operate under load." This got me looking into the purpose of the disconnect switches. I always thought they were required not only to lock-out tag-out, but also to turn off the motor and loads in the case of an emergency. But the code is explicitly saying do not use this switch when the load is live. So what should someone do in an emergency? They cannot use this switch right?
I am confused after reading this previous post on Mike Holt:
http://forums.mikeholt.com/showthread.php?t=146430
Then I read this link:
https://iaeimagazine.org/magazine/2...ans-for-motor-and-air-conditioning-equipment/
The first link says don't open a switch under load. The second link says, yes, do install and operate this switch under load. I am confused...
Also, section 430.109(E) talks about an isolating switch for motors over 100HP, but what about motors below this but above 2HP? Also, 430.109(E) says that the switch should be marked "Do not operate under load." This got me looking into the purpose of the disconnect switches. I always thought they were required not only to lock-out tag-out, but also to turn off the motor and loads in the case of an emergency. But the code is explicitly saying do not use this switch when the load is live. So what should someone do in an emergency? They cannot use this switch right?
I am confused after reading this previous post on Mike Holt:
http://forums.mikeholt.com/showthread.php?t=146430
Then I read this link:
https://iaeimagazine.org/magazine/2...ans-for-motor-and-air-conditioning-equipment/
The first link says don't open a switch under load. The second link says, yes, do install and operate this switch under load. I am confused...