Does that qualify as a disconnect for the motor though?I have installed several gate openers. They all had wall-wart type power supplies.
There are internal battery terminals you can disconnect to remove D.C. power.
The exception requires a lockable disconnect at the well motor controllerAre disconnects required for ALL motors?
Specifically asking about 12v automatic gate openers.
And while we're on the topic what about submersible pumps? If so why do you never see disconnects at well heads?
Yes i never considered this much but as far as i can remember NEC didn’t mention voltage rating as a condition to permit the absence of a motor disconnect.430.109(B) allows the branch circuit overcurrent device to serve as the motor disconnecting means for stationary motors of 1/8 horsepower or less.
Why no disconnect at well heads - check out 430.102(B) as well as the informational note that follows.
I see nothing that would disqualify any motor simply because it is 12 volts. You have to remember this disconnect isn't just for removing voltage hazards but also would not allow release of mechanical energy. A 12 volt motor may not have voltage hazard but can still have that energy from the output shaft when running.
I try to help with what I know on hand.In many cases answering Code questions without the Code is akin to providing the time when on e has no watch
Awaiting your return tom work (and book) it would be a great idea to sign up at NFPA and take advantage of the free access to the NEC
I can't remember what year they changed the rule a bit, maybe 2005 give or take a code cycle or two. But you used to be able to use the disconnect for the controller as the disconnect for the motor when not within sight of the motor if that disconnect had locking provisions. This was used a lot in situations with MCC's because your MCC bucket had a lockable disconnect and of course is the controller disconnect as well.Yes i never considered this much but as far as i can remember NEC didn’t mention voltage rating as a condition to permit the absence of a motor disconnect.
I do not have my NEC book but i do recall that under some situations that in order for the branch circuit breaker to serve as the motor disconnect it would have to be within sight or 50’ from the motor. Perhaps due to the 1/8 low hp this doesn’t apply here?
This post brings up a good point because many outdoor motors can be beyond 50’ from the breaker panel. So a disconnect would be needed
Also i would like to point out that one disconnect can serve multiple motors if its sized to code and proper horsepower rating
does current code allow a standard single gang “toggle” switch such as for lighting to be placed next to a 1/8 hp motor for the switch or allow the branch circuit breaker beyond 50’ from the motor to qualify as the motor disconnect. What if the motor has an integral motor mounted switch?1/8 hp or less has and still allows the branch circuit device to be the motor disconnect