Motor nameplate is 30 amps
Tables show 40 amps
Max breaker- inverse time can be 250% of 30 amps = 75 amps
Can I use a 60 amp disconnect with 70 amp breaker in it.
The disconnect needs to be 115% larger than the fla so 60 amp covers that and the breaker is only for short circuit and ground fault. The only thing I can come up with is 110.3
Is there an actual danger in doing this. This is totally hypothetical...
Tables show 40 amps
Max breaker- inverse time can be 250% of 30 amps = 75 amps
Can I use a 60 amp disconnect with 70 amp breaker in it.
The disconnect needs to be 115% larger than the fla so 60 amp covers that and the breaker is only for short circuit and ground fault. The only thing I can come up with is 110.3
Is there an actual danger in doing this. This is totally hypothetical...