You must always get the easy installs with no challenges, like the motor being 100 feet above grade but the motor control room is on grade and out of the dust, rain, whatever.In general there is a disconnect within 50' and within site so then VFD would generally be within 50'
Is there a maximum distance that a motor can/should be from the VFD? Specifically cooling tower motors 480v , 100HP, 112 FLA .
The longer the distance, the more you must contend yourself with capacitive coupling in the conductors, which then contributes to standing wave creation and motor EDM bearing damage, etc. etc. How long that distance is becomes a variable because of multiple factors that go into the equations. I have seen 15kM done with MV drives successfully with no motor problems, I've seen LV motors damaged from 25ft of improperly installed cables.
Many of which can be overcome by design but that involves additional cost. Filters, cable size, motor winding design, and so on. Borehole pumps obviously have to be located at the borehole and that can be some distance from the sub/switch-room where the drives are located. A few hundred metres in some cases. As I recall, the longest run we did was about 300 metres (1,000 feet) but is was only 75kW (100 HP) as I recall.as far as the code goes, no.
in practice, there are a number of factors that might tend to limit that distance.
Many of which can be overcome by design but that involves additional cost. Filters, cable size, motor winding design, and so on.
Yes, they were gapped autotransformers. The gap was to prevent saturation owing to any non-symmetrical component in the PWM waveform.I am surprised that a step up transformer between the PWM output and the motor can perform well. Are they custom transformers for the application?