When sizing equipment ground for a motor and the overcurrent device is much higher than the conductor rating, so the equipment ground size from Table 250.122 is actually more than motor conductor size. The exception say's E.G.C doesn't have to be larger than motor conductors. So another electrician in my shop tells me he knows there is another exception that allows for a smaller E.G.C. I can't seem to find it anywhere. Is this true? Also, we use H.M.C.P's. They are instantanous trip with a dial for different motor amperages. Like say a 100Amp HMCP you can increase the trip setting to fit a 75 hp. 3 phase motor or lower it for a smaller motor. So is the E.G.C. on these sized according to the calculation of motor full load from N.E.C. current times the setting? which would always end up using the exception and it would end up being the same as the motor leads. Or is it sized according to the 100Amp rating of the H.M.C.P? All motors in this facility use multi-conductor cable and the E.G.C's are smaller than the motor leads. Hope this isn't confusing to read!