PerNEC 430.250 a 100HP Induction type motor has a FLA of 124A. This requires #2/0 AWG THWN.
Thenameplate rating is only 109A. This requires #1/0 AWG THWN. (Yes, I did calculate this via the code requirements.)
Which takes precedence when sizing feeder conductors?
Please note: This is a speciality motor that cannot, and will not, ever be replaced by a "shelf" motor. If this motor ever fails, it will be rebuilt, or a new motor will be ordered from the original pump manufacturer.