Motor Feed calculations

Status
Not open for further replies.

kgk1961

Member
Location
Georgia, USA
PerNEC 430.250 a 100HP Induction type motor has a FLA of 124A. This requires #2/0 AWG THWN.
Thenameplate rating is only 109A. This requires #1/0 AWG THWN. (Yes, I did calculate this via the code requirements.)

Which takes precedence when sizing feeder conductors?

Please note: This is a speciality motor that cannot, and will not, ever be replaced by a "shelf" motor. If this motor ever fails, it will be rebuilt, or a new motor will be ordered from the original pump manufacturer.
 
Welcome to the Forum

Unless the motor falls under one of the exceptions in 430.6, and it does not appear to, you will need to use the Table value
 
PerNEC 430.250 a 100HP Induction type motor has a FLA of 124A. This requires #2/0 AWG THWN.
Thenameplate rating is only 109A. This requires #1/0 AWG THWN. (Yes, I did calculate this via the code requirements.)

Which takes precedence when sizing feeder conductors?

Please note: This is a speciality motor that cannot, and will not, ever be replaced by a "shelf" motor. If this motor ever fails, it will be rebuilt, or a new motor will be ordered from the original pump manufacturer.

The tables take into consideration the worst case efficiency or power factor at the horsepower values given.

You are likely to not even find a new 100 hp motor that has a FLA of 124 amps marked on it, but NEC wants to make sure a circuit designed for a 100 hp motor can handle any 100 hp motor that may be connected to it.
 