I have the following motors all running at the same time:
(qty)
(1) 75 HP 460V 3ph, 87 FLA
(2) 50 HP 460V 3ph 57 FLA
(1) ?HP 480V 3ph 615 FLA ( data was given to me, no HP)
A utility transformer will feed a 1200 amp CT cabinet with a main breaker. This will feed a distribution panel with a main breaker and breakers for each of the motors. I calculated the branch load breakers as follows from 430.52, all to be instantaneous trip.
87A*125% = 108.8 A -> 110A breaker
57A*125% = 71.25 A -> 80A breaker (2)
615A*125% = 768.7A -> 800A breaker
The feeder from the CT cabinet to the distribution panel i calculated from 430.24A as
=(615*125%) + 57 + 57 + 87 = 969.75A
then from table 310.16 (60 degree column for worst case) i use 3 sets of 1250 kcmil.
Feeder protection
The necessary breaker i calculated from 430.62 as 800 + 87 + 57 + 57 = 1001 Amps. So ill put a 1000 amp breaker in the distribution cabinet.
Does this look correct? im unsure of what to do since the 3 smaller motors are being controlled with an ABB VFD installed in an ABB bypass cabinet which allows the VFD to be taken out of service. The large motor is controlled by its own VFD.
Any input would be helpful.
Thanks
Ron
(qty)
(1) 75 HP 460V 3ph, 87 FLA
(2) 50 HP 460V 3ph 57 FLA
(1) ?HP 480V 3ph 615 FLA ( data was given to me, no HP)
A utility transformer will feed a 1200 amp CT cabinet with a main breaker. This will feed a distribution panel with a main breaker and breakers for each of the motors. I calculated the branch load breakers as follows from 430.52, all to be instantaneous trip.
87A*125% = 108.8 A -> 110A breaker
57A*125% = 71.25 A -> 80A breaker (2)
615A*125% = 768.7A -> 800A breaker
The feeder from the CT cabinet to the distribution panel i calculated from 430.24A as
=(615*125%) + 57 + 57 + 87 = 969.75A
then from table 310.16 (60 degree column for worst case) i use 3 sets of 1250 kcmil.
Feeder protection
The necessary breaker i calculated from 430.62 as 800 + 87 + 57 + 57 = 1001 Amps. So ill put a 1000 amp breaker in the distribution cabinet.
Does this look correct? im unsure of what to do since the 3 smaller motors are being controlled with an ABB VFD installed in an ABB bypass cabinet which allows the VFD to be taken out of service. The large motor is controlled by its own VFD.
Any input would be helpful.
Thanks
Ron