I read over this thread (http://forums.mikeholt.com/showthread.php?t=129894) but it sounds like Jraef is saying the cable in the MCC feeding the soft starter should be sized at the same ampacity as the rating of the MCC breaker. Doesn't NEC 430.62(A) allow otherwise?
Let's say I have a 100 HP, 460 V motor (124 A FLC) on a soft starter. The soft starter has 225 A fuses, which would be the branch SCPD. The soft starter is fed by a 300 A breaker in the MCC, which would be the feeder SCPD. Per NEC 430.62(A), I should be able to size the cable from the MCC to the soft starter at 125% of 124 A FLC = 2/0 AWG. Any disagreements?
Let's say I have a 100 HP, 460 V motor (124 A FLC) on a soft starter. The soft starter has 225 A fuses, which would be the branch SCPD. The soft starter is fed by a 300 A breaker in the MCC, which would be the feeder SCPD. Per NEC 430.62(A), I should be able to size the cable from the MCC to the soft starter at 125% of 124 A FLC = 2/0 AWG. Any disagreements?