jw441
400 HP Motor/Pump, 1800 SYNCH SPD(rpm), 3 PHASE, 60 HZ, 460 VOLT, 445 FLA, 2900 LOCK ROTOR, INS CLS & KVA/HP CODE "F", DESIGN "B", 89 FL(pwr factor), US ELEC MTRS, PENTAIR PUMP GROUP.
BLUE PRINT CALLS OUT(using THHN copper): 3 - 350kcmil, 1 - #1/0 GND, 2 - 3.5" C (parallel feed) - C/B 800 AF / 800 AT to VFD(controller), then back out again(parallel feed of same) to Motor/Pump.
MY CALCULATIONS: 3 - #3/0, 1 - #1 GND, 2 - 2" C (parallel feed) from C/B 600 AF / 600 AT to VFD(controller); then 3 - 250kcmil, 1 - #1 GND, 2 - 2.5" C (parallel feed of larger) from VFD to Motor/Pump.
____________________________________________________________
200 HP Motor/Pump, 1800 SYNCH SPD(rpm), 3 PHASE, 60 HZ, 460 VOLT, 224 FLA, 1309 LOCK ROTOR, INS CLS & KVA/HP CODE "F", DESIGN "B", 87.6 FL(pwr factor), US ELEC MTRS, PENTAIR PUMP GROUP.
BLUE PRINT CALLS OUT(using THHN copper): 3- 350Kkcmil, 1 - #2 GND, 1 - 3" C (single feed) - C/B 600 AF / 500 AT to VFD, then back out again (single feed of same) from VFD to Motor/Pump.
MY CALCULATIONS: 3 - #3/0, 1 - #4 GND, 1 - 2" C (single feed) from C/B 300 AF / 300 AT, to VFD(controller); then 3 - 250kcmil, 1 #4 gnd, 1 - 2.5" C (single feed of larger) from VFD to Motor/Pump.
PLEASE ASSIST AND/OR ADVISE TO ANY/ALL.
ANY/ALL CORRECT ADJUSTMENTS(99' NEC) ARE APPRECIATED.
THANK YOU - FRATERNALLY, JW441
[/b][/u]
[/b][/u]