A motor feeder from a switchboard feeds a single induction motor load, with a combination circuit breaker-type motor starter mounted at the motor. Power factor correction capacitors are connected on the load side of the starter parallel to the motor.
How is the ampacity of the motor feeder conductors calculated? 430.27 directs me to 460.8 and 460.9, which do not really apply to the feeder. Am I required to size the conductors at 1.25 x FLA?