MrJLH

Senior Member
Location
CO
:blink:Had a pump trip out yesterday. Opened the NEMA 7/9 enclosure and found significant damage to the feeder cable at the breaker connections. Is this a cause of the enclosure getting too hot? Typically we run this pump right at FLA. Any ideas?

cracking.JPG

Capture 2.JPG
 
Last edited by a moderator:
If the conductors are the proper size then I would guess that it's terminal failure likely due to improper torque.
 
My Money is on undersized wire, overheated wire terminations.

Everyone forgets the motor load adjustment x 1.25
 
Usually if the terminations over heat, there is significant discoloration and evidence of thermal damage to the breaker. I don’t see that here.

There is something odd about those cables though. It almost looks like the insulation was taped on and it’s the tape that is failing. Maybe it’s just my old eyes on a small phone screen though b
 
Usually if the terminations over heat, there is significant discoloration and evidence of thermal damage to the breaker. I don’t see that here.

There is something odd about those cables though. It almost looks like the insulation was taped on and it’s the tape that is failing. Maybe it’s just my old eyes on a small phone screen though b

And is it just me or does B phase appear to be aluminum while A and C are copper?
Never mind I think its just dust (some on top of breaker as well)
 
B phase has a problem looks like oxidation, look at the phase tape the pipe is a chimney for the heat; as said need to calculate load/wire size and ir and amp check .
 
Have you had a chance to do an amp draw or IR scan on this with the pump running?


Unfortunately no, our facility does not perform I/R scans in Nema 7/9 enclosures on a program type basis. I have been pushing this though.

however, I did find a photo of the breaker from last year around this time and there was no apparent cracking in the cables.
 