440.22(b) (1)
440.22(b) (1)
Originally Posted by faranca77
Each breaker have thermal trip to disconnect the main panel at over load case, short circuit trip (electromagnet trip) to disconnect at the short circuit case.
For main panel feed more than motor-compressor I will apply Section 440.22(B) (1) to size the main breaker
And For main panel feeding lighting and receptacle circuits I will apply Section 215.3
1-Is Section 440.22(B) (1) in the national electrical code to size the main breaker according to thermal trip or short circuit trip?
If the answer according short circuit trip why the national electrical code don?t size according to the thermal trip???
If the answer according short circuit trip is this correct to size the breaker according to short circuit calculation which depend on impedance accumulation
I (sort circuit) =voltage (line to line)/total impedance/1.73
2-Is Section 215.3 in the national electrical code to size the main breaker according to thermal trip or short circuit trip?
If the answer according short circuit trip why the national electrical code don?t size according to the thermal trip???