chevyx92
Senior Member
- Location
- VA BCH, VA
I have been giving the following info for a new install. New RTU will have an MCA of 98A 3Phase 208V with Max Fuse Size listed at 125A. There will also be an indoor blower motor rated at 1.5HP 208V single phase. 430.248 shows that motor to be 11 amps.
Scoped job out and found a nearby 3 phase 208V feeder not being used. It has #2 CU coming into a Non Fused 200A disconnect which is fed from a 400A Fused disconnect with 250A fuses installed.
My questions are:
1) With an MCA of 98 amps do you think I can get by fusing at 100A instead of 125A? I ask only because there's an existing 100A Fused disconnect there not being used I could possibly use. If I have to fuse at 125A then I will have to install
a 200A fused disconnect with 125A fuses.
2) Is the #2 CU code compliant to feed both these motors? I think so. MCA of 98A plus the 11A of blower motor = 109 A #2 CU is good for 115 A
3) Feeder OCPD. According to 430.62 if I take the largest motor rating which is the RTU of 98A plus 125% = 122.5A plus 100% of all other motor loads, blower is 11A that would equal = 133.5A Correct?????
4) If 133.5A is correct then we fuse down right? Which means the feeder OCPD would be set at 125A? Right?
Scoped job out and found a nearby 3 phase 208V feeder not being used. It has #2 CU coming into a Non Fused 200A disconnect which is fed from a 400A Fused disconnect with 250A fuses installed.
My questions are:
1) With an MCA of 98 amps do you think I can get by fusing at 100A instead of 125A? I ask only because there's an existing 100A Fused disconnect there not being used I could possibly use. If I have to fuse at 125A then I will have to install
a 200A fused disconnect with 125A fuses.
2) Is the #2 CU code compliant to feed both these motors? I think so. MCA of 98A plus the 11A of blower motor = 109 A #2 CU is good for 115 A
3) Feeder OCPD. According to 430.62 if I take the largest motor rating which is the RTU of 98A plus 125% = 122.5A plus 100% of all other motor loads, blower is 11A that would equal = 133.5A Correct?????
4) If 133.5A is correct then we fuse down right? Which means the feeder OCPD would be set at 125A? Right?