malachi constant
Senior Member
- Location
- Minneapolis
I'm the engineer on this one. Renovation of existing building, the inspector is making us bring the elevator up to code (NEC '08). In the course of performing some of the flagged upgrades the electrician noticed there is not presently a ground conductor from the existing panel to the existing elevator disconnect switch. I directed him to pull a new ground. His foreman tried but was unable to without pulling out the wiring.
The options are:
(A) Pull out the old wiring and pull in new 130' feeder w/ ground. OR
(B) Use the existing IMC as ground, which he has visually inspected for solid connections and confirmed is bonded at the distribution panel.
I looked at elevator article 620 sections VII (OCP) and IX (grounding) and confirmed they don't require anything unusual - deferring to article 430 part V, and article 250 parts V and VII, respectively.
All that to say I readily admit grounding is not my area of expertise, but this doesn't look like too tricky of a question. Just want to make sure I don't (A) waste owner's money on something not required by code, or (B) direct the contractor do do something that does not meet code.
Any help? Thanks!
The options are:
(A) Pull out the old wiring and pull in new 130' feeder w/ ground. OR
(B) Use the existing IMC as ground, which he has visually inspected for solid connections and confirmed is bonded at the distribution panel.
I looked at elevator article 620 sections VII (OCP) and IX (grounding) and confirmed they don't require anything unusual - deferring to article 430 part V, and article 250 parts V and VII, respectively.
All that to say I readily admit grounding is not my area of expertise, but this doesn't look like too tricky of a question. Just want to make sure I don't (A) waste owner's money on something not required by code, or (B) direct the contractor do do something that does not meet code.
Any help? Thanks!