I'm trying to understand the rules for conductor and OCPD sizing for feeders supplying motors and possibly other loads.
In particular, 430.62 (Part V) on a feeder with just motor loads seems straightforward enough. 430.62(A) says if you size your conductors based on the motor rules in 430.24, then the OCPD for the feeder "shall be provided with a protective device having a rating or setting not greater than" an expected motor-type computation. And 430.62(B) says that if you size your conductors "normally", then you can select your OCPD "normally".
However 430.63 "Rating or Setting — Motor Load and Other Load(s)" uses the language that "the feeder protective device shall have a rating not less" an expected motor-type computation. That would make sense if some other rule provided a link between the feeder conductor size and OCPD size. But 240.4(G) exempts 430.63 from the usual 240.4 rule on OCPD vs conductor size.
Thus it would appear that for a feeder supplying motor loads and other loads, the conductors could be sized by 430.24, and there is no limit on the OCPD size. Which makes no sense, so what I am missing?
Cheers, Wayne
In particular, 430.62 (Part V) on a feeder with just motor loads seems straightforward enough. 430.62(A) says if you size your conductors based on the motor rules in 430.24, then the OCPD for the feeder "shall be provided with a protective device having a rating or setting not greater than" an expected motor-type computation. And 430.62(B) says that if you size your conductors "normally", then you can select your OCPD "normally".
However 430.63 "Rating or Setting — Motor Load and Other Load(s)" uses the language that "the feeder protective device shall have a rating not less" an expected motor-type computation. That would make sense if some other rule provided a link between the feeder conductor size and OCPD size. But 240.4(G) exempts 430.63 from the usual 240.4 rule on OCPD vs conductor size.
Thus it would appear that for a feeder supplying motor loads and other loads, the conductors could be sized by 430.24, and there is no limit on the OCPD size. Which makes no sense, so what I am missing?
Cheers, Wayne