I was trying to understand the hazardous classifications of a gas station. If you've got one pump, do you got 20' out from any corner of the dispenser? How far up from the dispenser is class 1 div 2? I'm looking in NEC 514 but need help interpreting. I'm trying to install light fixtures but need to know what type to install.
 

dillon3c

Senior Member
Re: Motor Fuel Dispensing Facilities

Extending 18" horizontally from the four sides of the dispenser,extending up to level vertically, of the dispenser height.*See figure 514.3 page 70-394 of '05

*Luminaires,wet/damp location..~410.4(a)

Edited: haven't seen canopy in the newer installations of the super-pumpers,that are designed in a way of the trapping of vapors.Generally of the -flat- design..