Re: Motor fuel dispensing facilities
Bnd,
In my first reply, I asked if you were actually using Zone rather than Division electrical area classification. I was referring to that original query in my next reply. It is now clear you are indeed using Zones. In that case, I?m curious what standard was used to develop the electrical area classification since Article 514 doesn?t recognize Zones. In fact, you can make a very strong case that the sump beneath the dispenser is Zone 0.
In any case, for this discussion, let?s simply assume the entire area classification was developed from 514.3(B)(1) with Zone 1 = Division 1 and Zone 2 = Division 2. Let?s also assume the dispenser is listed per UL 87. That covers a lot of internal wiring issues that we won?t have to deal with here. I am also making a final assumption that all field wiring is through the terminal box in question and only terminals are actually in the enclosure. Clarify if any of these assumptions is incorrect.
Don and I have both made the point that a single, properly installed, seal may cover all requirements for both flame propagation and gas migration reduction. Those requirements are that the flame propagation seal be no more than 18? from the enclosure and all intervening fittings between it and the enclosure be identified for the area classification. Second, the boundary seal can be as much as 10? from the boundary, but no intervening threads, except an explosion-proof reducer at the seal, is permitted between the boundary seal and the boundary. If either of these conditions are not met, two seals are required.
I would also like to add one thing to the list of potential human errors/hazards Don pointed out. For an otherwise properly installed enclosure, a single scratch on the ground surface of [edited here] a ground-flange type cover may be enough to destroy the enclosure. Most ?type d? enclosures actually use threaded covers but flanged type are also recognized. BTW if the enclosure is only ?type e? and not ?d, e? an internal ignition, though rare, could still be propagated externally and no seal would stop it.
[ June 01, 2004, 10:21 AM: Message edited by: rbalex ]