ptonsparky
Tom
- Occupation
- EC - retired
Small fuel tanks now require a containment system around them and essentially are an open box that the fuel tank sits in. The dispenser is mounted to the top of the tank. I have not measured the one we will be working with but will guess that it is about 24" tall and hopefully the wall to wall dimensions to the tank are >= to 18" on all sides. That being True would indicate to me that the area outside that box is not a Hazardous area. Ref: 514.3(B)(1) and Fig 514.3(B). 2014 NEC.
Yes, No?
Yes, No?