B bbanzai Member Location Clearfield Utah Dec 5, 2005 #1 Can anyone give me some guidance on sizing service conductors for a 150 hp 3 phase/delta motor generator? The m/g set provides power to a communication site. Do I size from the motor table and the 1.25 rule?
Can anyone give me some guidance on sizing service conductors for a 150 hp 3 phase/delta motor generator? The m/g set provides power to a communication site. Do I size from the motor table and the 1.25 rule?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Dec 6, 2005 #2 Re: motor generator set I would suggest that the supply conductors be sized per 430.22 and the output conductors per 445.13. Don
Re: motor generator set I would suggest that the supply conductors be sized per 430.22 and the output conductors per 445.13. Don
B bbanzai Member Location Clearfield Utah Dec 6, 2005 #3 Re: motor generator set Thanks, That is what I did. I used table 430.150 and did it just like it was a feeder circuit. Thanks for the help.