bbanzai

Member
Location
Clearfield Utah
Can anyone give me some guidance on sizing service conductors for a 150 hp 3 phase/delta motor generator? The m/g set provides power to a communication site. Do I size from the motor table and the 1.25 rule?
 
Re: motor generator set

I would suggest that the supply conductors be sized per 430.22 and the output conductors per 445.13.
Don
 