motor generator set

Status
Not open for further replies.

bbanzai

Member
Location
Clearfield Utah
Can anyone give me some guidance on sizing service conductors for a 150 hp 3 phase/delta motor generator? The m/g set provides power to a communication site. Do I size from the motor table and the 1.25 rule?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: motor generator set

I would suggest that the supply conductors be sized per 430.22 and the output conductors per 445.13.
Don
 
Status
Not open for further replies.
Top