First post here, and not a big social media user but I have an issue that I'd like some good feedback on from the electrical community at large.
Here's the specs:
Single phase motor. 1 HP. Dual voltage 120/240. Motor running at 240V.
Here's the installation:
Boat lift. Typically two motors controlled by a manufactured controller containing contactors to shift motor direction.
Controller does not require a neutral.
Here's the issue:
After a year or two some of these installations are developing ground faults at the motors. GFCI circuit breaker does it's job and opens. I'm not sure why the lifetime is so brief for some of these motors. Is is abuse to the motor and possible insulation is lost on the motor windings resulting in a case ground fault? Is is environmental factors like moisture or debris in the motor? Lack of use and the motor develops internal corrosion issues? Cheap motors? Owners applying corrosion block to external case? These all seem like probable reasons for potential ground faults but tough to verify unless totally obvious issues exist.
It is impractical to disassemble a small motor like this in the field to look for gremlins. Overall the motors are pretty well protected the way they are installed in the application. At the risk of answering my own question, can we probably attribute this issue to mis-use of the motor causing premature failure?
BTW if the GFCI protection is removed 99.9% of the time the motor(s) run completely in spec.
Any suggestions for general testing guidelines?
Thanks to anyone who has any helpful insight or feedback to this matter.
Here's the specs:
Single phase motor. 1 HP. Dual voltage 120/240. Motor running at 240V.
Here's the installation:
Boat lift. Typically two motors controlled by a manufactured controller containing contactors to shift motor direction.
Controller does not require a neutral.
Here's the issue:
After a year or two some of these installations are developing ground faults at the motors. GFCI circuit breaker does it's job and opens. I'm not sure why the lifetime is so brief for some of these motors. Is is abuse to the motor and possible insulation is lost on the motor windings resulting in a case ground fault? Is is environmental factors like moisture or debris in the motor? Lack of use and the motor develops internal corrosion issues? Cheap motors? Owners applying corrosion block to external case? These all seem like probable reasons for potential ground faults but tough to verify unless totally obvious issues exist.
It is impractical to disassemble a small motor like this in the field to look for gremlins. Overall the motors are pretty well protected the way they are installed in the application. At the risk of answering my own question, can we probably attribute this issue to mis-use of the motor causing premature failure?
BTW if the GFCI protection is removed 99.9% of the time the motor(s) run completely in spec.
Any suggestions for general testing guidelines?
Thanks to anyone who has any helpful insight or feedback to this matter.