neceltic
Member
- Location
- Omaha, NE, USA
I am a little confused by motor circuit grounding as listed in 250.122(D). 250.122(D)(1) is straightforward and points to using Table 250.122 for motor ground sizing. However, 250.122(D)(2) seems to say that if one has an instantaneous trip breaker then the ground has to be sized for the maximum fuse allowed using 430.52(C)(1). This would increase the grounds in larger HP motors. The particular problem is my customer uses cabled products so an upsized ground would mean a non-standard cabled product. The AHJ's opinion is that (D)(2) takes precedence over (D)(1). I haven't heard of this from any other inspectors, customers or vendors. Has anyone ran across this before? Explanation of the code's intent?