ANNUAL MOTOR TEST
We are required to do a motor electrical ground test annually.
Here is how we have been told to do it and was wondering if it was a standard.
Doing the test on each piece of equipment.
Meter type: Analog ? Digital (Analog is best)
Meter Setting: At the time of each motor test
Meter Reading: At the time of each motor test.
The length of the wire used for a lead.
The size of the wire used for a lead.
The resistance of the lead wire.
The voltage to ground reading to each motor.
The incoming voltage to each motor.
The fuse/breaker size to each motor.
Testing method of each piece of equipment.
Equipment frame to the source of power. (This could be at the MCC or it could be at the service panel.)
1. Find the voltage to ground reading.
2. Ohm reading from equipment frame to source.
3. The resistance of the lead wire.
4. Subtract line 3 from line 2. This is actual ohms.
5. Divide line 4 into line 1. This is the amps to ground.
6. Amps to ground should be 9 to 10 times greater than fuse/breaker size.