Motor insulation values when measured from starter bucket

Status
Not open for further replies.

philly

Senior Member
I was wondering why insulation readings for motors were less when using a megger to measure at the starter bucket and including the cables and motor as opposed to just testing the motor?

For instance when testing a motor alone we have lets say 100Meg L-g. And when testing cables we have lets say 50Meg L-G. However when we measure from the starter bucket testing both cables and motor we have lower values of lets say 25Meg L-G.

Why do we see lower values when measuring a combination in comparison with measuring the motor and cables seperately?
 
I was wondering why insulation readings for motors were less when using a megger to measure at the starter bucket and including the cables and motor as opposed to just testing the motor?

For instance when testing a motor alone we have lets say 100Meg L-g. And when testing cables we have lets say 50Meg L-G. However when we measure from the starter bucket testing both cables and motor we have lower values of lets say 25Meg L-G.

Why do we see lower values when measuring a combination in comparison with measuring the motor and cables seperately?

Paralell paths for leakage current. (R1*R2)/(R1+R2)= Total resistance (Really leakage current, you cant measure resistance)
 